Inverter chargers

This topic contains 2 replies, has 2 voices, and was last updated by  J J 3 years, 4 months ago.

Viewing 3 posts - 1 through 3 (of 3 total)
  • Author
    Posts
  • #28451

    J J
    Member

    OK solar experts, if I install a inverter with a charger how do I prevent the charger / converter in the RV from also trying to charge the batteries at the same time. I have a 4 stage 65A charger built into the RV converter, it’s a Progressive Dynamics unit..

     

    John

    #28477

    Eddie & Aileen
    Participant

    Hi JJ, you can just turn off the beaker to the Progressive Dynamics unit. Then if you need to isolate the inverter/charger if you put the RV in storage mode or something was to go wrong with the combo unit you could just flip the beaker on to the PD unit and still charge the battery bank.

    Happy Trails!!!:good:

    #28634

    J J
    Member

    Thanks Eddie, think I will do like most folks and start to assemble the parts and perhaps next year will do a self install.

     